Cudedog wrote:Bethers wrote:Deeann, up until a year or so ago I'd agree about the parks without the 15 amp connection, but I'm seeing more and more of them now ... probably as more upgrade to 50 amp.
Thank you Beth and Deeann.
I do have some basic understanding of electricity (with my set up I need to be aware of - and calculate - the amps/volts/watts of my devices so as to not "go over" the rating of my extension cord) , although not much regarding RV hookups, and this discussion is being extremely helpful.
Another question:
Say I am at a site that has hookups for both 15 amps and 30 amps on the pole. Say I put an adapter on the 30 amp receptacle to step it down to 15 amps, and then plug into both the 15 amp and stepped-down 30 amp receptacle. Can I then safely pull 15 amps from
each receptacle (volts and watts also being in the acceptable range) at the same time?
Not sure I am asking this correctly, but responses appreciated.
Thank you!
Anne
To answer your question above: Yes. You should be able to do this. Just go ahead and plug into both outlets. If you pull too much current the circuit breaker on the pole will trip then you'll have to shut something off in your van. Then reset the breaker and you should be fine.
Now, you might ask this: If your cable is rated for 15 amps and you plug into a 15 amp outlet, the circuit breaker at the pole will trip if you try to pull more than 15 amps. This is good. This is what you want to happen. The circuit breaker is protecting your cable and your converter. BUT, when you put an adapter on your 15 amp cable so that you can plug it into a 30 amp outlet, that breaker won't trip until you try to pull more than 30 amps through it. Now you have a problem because the outlet is letting you pull 30 amps over your 15 amp cable!!! YOWZA! Your cable won't handle 30 amps so it will melt and possibly start a fire! How do you prevent this? You have a 15 amp breaker in your power converter. That's how. Your onboard breaker will protect your cable and your converter regardless of which outlet you are plugged into.
So, you can plug into either outlet, 15 or 30 amp, and you can use both at the same time.
An example: It's cold. You have a space heater on in the van. It pulls around 14 amps. You want to use your electric grill. If you plug the grill into the rv, you'll pop the breaker because you're trying to pull more than 15 amps through your converter. So go plug the grill in at the pole. Problem solved..
TIP: If you want to use a small space heater, buy one that has a low, medium and high setting. If you use the high setting you'll be pulling around 14 amps and you'll be close to your limit. If you turn anything else on the breaker will likely trip. But if you use the medium setting you will be pulling less current and you'll be able to turn on a light or your tv, etc. while the heater is running. Hence, you can have some heat and still use some other things in your van.
Has this answered your question? I know electricity is confusing. I could explain it so much better if I was there with you. Hope my answers aren't confusing you or any of the other gals.